Srinivasa Rao Samineni
12/01/05 04:57
Read: 604 times
Hyderabad
India


 
#104483 - weigh feeder details
Responding to: Srinivasa Rao Samineni's previous message
Thanks for ur replies

I dont know much about mechanics but Mech. Engineers says that the vibration is very less.
I am using LTC2420 20 bit delta sigma ADC and taking 5 samples per second. If the belt is in stop condition i am getting steady ADC count (neglecting lower 8 bits & 30 point moving average filter) while belt running around 300 count variation is coming. Of course it may be from that minimum belt vibration.
I have checked the same weigh feeder and loadcell amplifier with different weigh feeder controllers they are working fine.

Waiting for replies

Regards
srinivas



List of 13 messages in thread
TopicAuthorDate
about weigh feeder      Srinivasa Rao Samineni      11/26/05 01:45      
   Lack of details      Terry Lingle      11/26/05 06:34      
      "Cleverer"      Steve M. Taylor      11/27/05 07:39      
         Yes that would improve response time      Terry Lingle      11/27/05 08:24      
            so would I      Steve M. Taylor      11/27/05 10:24      
   weigh feeder details      Srinivasa Rao Samineni      12/01/05 04:57      
      Could it be induced noise?      Valentin Angelovski      12/01/05 05:39      
      ur uhm      Terry Lingle      12/01/05 09:09      
         the easy test      Erik Malund      12/01/05 09:30      
            Good point Erik      Terry Lingle      12/01/05 09:53      
      Do I miss something?      Kai Klaas      12/01/05 11:05      
         I agree      Srinivasa Rao Samineni      12/01/05 22:49      
            Dampening      Kai Klaas      12/02/05 05:38      