Ap Charles
05/24/12 02:13
Read: 899 times


 
#187487 - Sensor installing
we need to install sensor on a storage steel tank, containing motor oil which is tied to protective earth(PE) . The sensor is hydrostatic type oil level sensor but its steel body is tied to internal GND. Is there any problem in installing such a sensor for oil level monitoring. The sensor powersupply and its outputs are totally isolated at instrumentation side. Should we expect ground loops getting developed between the internal GND and PE.
http://www.8052.com/users/apc/11se.JPG

Rgds
-Ap

List of 15 messages in thread
TopicAuthorDate
Sensor installing      AP Charles      05/24/12 02:13      
   EX question ?      Kai Klaas      05/24/12 06:04      
      Manufacturer      AP Charles      05/24/12 07:53      
         Never tested? So not certified?      Per Westermark      05/24/12 09:08      
            Is it undesirable      AP Charles      05/24/12 10:05      
               As far as I know...      Kai Klaas      05/24/12 12:37      
                  No No..      AP Charles      05/24/12 13:32      
                     I agree...      Kai Klaas      05/25/12 10:39      
                        safety      AP Charles      05/28/12 02:01      
                           Yes and no...      Kai Klaas      05/28/12 16:48      
                              Looking for Pre-Boxed Solutions      Michael Karas      05/28/12 18:02      
                                 pre-boxed solutions .. no      AP Charles      05/28/12 23:53      
                                    But there's more to do...      Kai Klaas      05/29/12 05:40      
                                       not familiar with 'EX'      Erik Malund      05/29/12 06:41      
                                       Yes      AP Charles      05/29/12 07:25      